I keep getting this alarm on multiple different cut files now
Welcome to the forum.
Hard limit means the connection with the switch is likely loose if the actual switch is not being pressed.
Those switches are normally closed so when they are activated or the wire is not connected, it will consider that the switch is being pressed. So look for the continuity of the wires from the enclosure all the way to each switch and the actual connection at the switches. Bend and move the wires and see if the continuity changes.
Or it could be dirt or loose connection of the plug on the enclosure.
If you don’t find anything with the external wiring then it is a faulty switch (perhaps broken) or there is a loose connection in the enclosure.